Hi Beety,
Ok, so I will point out the errors for you....
When it comes to cable sizing it is obvious you have not got a clue. Online calculators will not help you either.. It is not as simple as you think..
For a start off, you do not size a cable according to the load, so it is not as simple as you think. You size a cable according to lots of things.
What is the load on the circuit??
What size, and TYPE of OCPD [Overcurrent protection device] are you going to use?
Next there are a load of "correction factors" for such things as ambient temperature, cable grouping, thermal insulation the cable might pass through, and type of OCPD too.
You calculate these factors, and apply them to the rating of the OCPD. You will find that the cable very often has to be rated for a substantially larger current than the rating of the OCPD itself.....
Then you have to decide what "disconnection times" are applicable to the type of circuit in the event of an earth fault.
Next you need to figure out the max figure for "earth fault loop impedance" allowable for the OCPD you have selected, in order to achieve the disconnection times you require.
You then need to figure out Ze for the supply, and then the value of R1 + R2 for your circuit, and then see if the resultant figure for Zs complies with the above, bearing in mind that the resistance of conductors increases with heat, and you have to make sure that it will be within permissible limits at the cable temperatures reached during a fault, NOT at room temperature..
Now you have to decide if the cable is suitable from the point of view of VD.
Next you have to see if the cable CPC is sufficient from the point of view of thermal effects in the event of a fault. Google the "adiabatic equation"
Oh, and if the cable CPC has to double as a bonding conductor there is another whole lot of fun to be had..
If your circuit is to comply, than ALL this needs to be checked..
Oh, and if you do all this, and the cable is the wrong type for its environment it will still not comply
See any of this in your "online calculator"????
As you can see, it is a piece of piss to be an electrician, anyone can do it... [NOT!!]
john..
Ok, so I will point out the errors for you....
When it comes to cable sizing it is obvious you have not got a clue. Online calculators will not help you either.. It is not as simple as you think..
For a start off, you do not size a cable according to the load, so it is not as simple as you think. You size a cable according to lots of things.
What is the load on the circuit??
What size, and TYPE of OCPD [Overcurrent protection device] are you going to use?
Next there are a load of "correction factors" for such things as ambient temperature, cable grouping, thermal insulation the cable might pass through, and type of OCPD too.
You calculate these factors, and apply them to the rating of the OCPD. You will find that the cable very often has to be rated for a substantially larger current than the rating of the OCPD itself.....
Then you have to decide what "disconnection times" are applicable to the type of circuit in the event of an earth fault.
Next you need to figure out the max figure for "earth fault loop impedance" allowable for the OCPD you have selected, in order to achieve the disconnection times you require.
You then need to figure out Ze for the supply, and then the value of R1 + R2 for your circuit, and then see if the resultant figure for Zs complies with the above, bearing in mind that the resistance of conductors increases with heat, and you have to make sure that it will be within permissible limits at the cable temperatures reached during a fault, NOT at room temperature..
Now you have to decide if the cable is suitable from the point of view of VD.
Next you have to see if the cable CPC is sufficient from the point of view of thermal effects in the event of a fault. Google the "adiabatic equation"
Oh, and if the cable CPC has to double as a bonding conductor there is another whole lot of fun to be had..
If your circuit is to comply, than ALL this needs to be checked..
Oh, and if you do all this, and the cable is the wrong type for its environment it will still not comply
See any of this in your "online calculator"????
As you can see, it is a piece of piss to be an electrician, anyone can do it... [NOT!!]
john..