Hi
I am studying to be an electrican and I quite often set myself some challenges to see if i'm learning well.
My mate is wanting to run a new supply to his garage. So I thought I would do some calculations to see if I can work out the cable required correctly. Could someone tell me if I am correct with my answer.Also there are a couple of questions at the end as well.
He has a TNCS 230v supply
His usage will be about 8.48KW (he has a lot of power tools and three ponds for koi)
It we be run from a 17th edition consumer unitin the house. So I thought use a 40amp MCB.
From consumer unit in house to consumer unit in garage is about 25 meters.
The cable would be a swa thermosetting cable clipped directly to the wall.
Ive worked out that he should use a 4mm cable. Would you agree?
Also ive seen on previous threads not to connect the earth to the earth on the house, to create a new earth path from the garage using an earth rod in the ground. Is this correct? and if so what is the reason behind it.
And also would you use a 2 core cable? if so would you connect the armoured cable to the earth on the garage side and not the house side?
If I have missed anything please let me know.
behind
I am studying to be an electrican and I quite often set myself some challenges to see if i'm learning well.
My mate is wanting to run a new supply to his garage. So I thought I would do some calculations to see if I can work out the cable required correctly. Could someone tell me if I am correct with my answer.Also there are a couple of questions at the end as well.
He has a TNCS 230v supply
His usage will be about 8.48KW (he has a lot of power tools and three ponds for koi)
It we be run from a 17th edition consumer unitin the house. So I thought use a 40amp MCB.
From consumer unit in house to consumer unit in garage is about 25 meters.
The cable would be a swa thermosetting cable clipped directly to the wall.
Ive worked out that he should use a 4mm cable. Would you agree?
Also ive seen on previous threads not to connect the earth to the earth on the house, to create a new earth path from the garage using an earth rod in the ground. Is this correct? and if so what is the reason behind it.
And also would you use a 2 core cable? if so would you connect the armoured cable to the earth on the garage side and not the house side?
If I have missed anything please let me know.