The earthing arrangement might require the SWA to be on an RCD. What is the earthing arrangement?
Last edited by a moderator:
wow... done your own research and got your answer. well done. now just to do more of that in future. but just remember that the OSG is just a guide and contains a very small selection from the book, it will be in there in a lot more detail of which cables require which protectionI Read a good section in the on site guide 7.2.5 its mentioning socket circuits and cables withouta metal covering need rcd an armoured has a metal cover so an armoured doesnt need it.manator your post what a coincidence you mentioned 2 core i was going to give my mate the armoured to do the job a 2 core 4mm i have got ive had it in storage.i would prefer 3 core.manator i would say use the armour as an earth and it doesnt need rcd
Correction - in most cases it is acceptable to use the SWA as the CPC. Not all cases.the armour is suitable as a CPC... so why go to the extra expense of an extra core? i rarely ever use a core as an earth, unless its there an not being used
Just who exactly from the DNO gave you that permission to change the definition of exporting an earth to calling it extending the EZ,?I wouldn't export the earth I would extend the equipotential zone to the garage.
Do you mean an Ra of 0.16?Just who exactly from the DNO gave you that permission to change the definition of exporting an earth to calling it extending the EZ,?
You can only extend an EZ to an adjoining building, not half a mile down the road,  :shakehead
How big is this Faraday cage you are building that can surround the cable route and encompass the garage and dwelling without being broken?
Btw,
I have a rod with a Ze of 0.16
For those that are unable to understand Ra
No, I mean a Ze,Do you mean an Ra of 0.16?