Hi all,
Out of interest, i thought i would post this...
A few days ago i was doing a bit of an install. [A second DB fed from a first one]
First off, if i measure loop impedance with my Megger 1730, it makes no difference whether i use the no-trip or high current settings. WHAT WILL make a difference, is how i connect it........
If you just stuff the probes on the terminals and hold them, you are likely to get variable readings, as it is IMPOSSIBLE for you to hold them perfectly still for the duration of the test.... Clip them on with the croc clips, [however awkward this may be] and you will get MUCH more consistant readings...
Anyway.....
Now, i measured Zs at the first board. I measured R1 + R2 for the cable, but when i measured Zs at teh second board, it was much higher than i had expected.... Still ok, but i am not he sort to think "that will do" If i get an unexpected reading, i want to know why....
I was well confused.... I did the testing myself, i installed it myself, so i knew there were no bad joints...
Hmmmmm, now then.....I had fitted an RCCB [a four pole one] at the start of the cable, adjacent to the first DB....
I wonder...... Now, it turns out, and i did the test MANY times, on all three phases too, that if you took a reading BEFORE the RCCB [right next to it] and then took a reading AFTER the RCCB [again, right next to it] that the reading after the device would be exactly .24 ohms higher. As i say, i did the test loads of times too.
I tried just measuring the resistance across the device too, perfect.... Sooooo, it is something to do with the internal wiring inside the RCCB when it is "in operation" as it were..
I left a note stuck to the door of the second DB, just to help others that may come after me, to tell them that if they want to check Zs, to link out the RCCB at the first board, or the reading will be incorrect, .24 ohms too high.
Whether the impedance of the device is higher than its resistance, or whether it is the way the meter works i have no idea..... Interesting though..
john..