This might get interesting - or I`ve had a "brain fart", and am starting to lose the plot.............
Imagine an intake panel for a TPNE TNC-S; 800A/phase property; metallic in structure.
On one end is a serviceway; with ten SWAs of various sizes, terminated to the top surface, running vertically down to their respective fuses. (from 50mm up to 150mm 4 core)
There are both Neutral and earth busbars running down the side, and along the bottom, of the chamber.
The earth busbar is, at regular intervals, bolted to the chassis. The neutral is bolted to the earth, through insulating spacers.
If I clamp the earth busbar where I can get the jaws around it, I can read a maximum of 28A returning current - I can clamp around two of the supports for the busbar - each one has in excess of 3A flowing between the busbar and chassis.
I cannot clamp around all of the individual earth cables which attach to the busbar (due to proximity to other cables).
I cannot isolate ANY of the outgoing circuits.
I did manage to clamp the supply cables (including neutral), and found 2 with approx 5A each "missing".
This still leaves me with around 18A (at least) unaccounted for.
Thoughts / suggestions would be appreciated ...........:coffeeheadbang
Imagine an intake panel for a TPNE TNC-S; 800A/phase property; metallic in structure.
On one end is a serviceway; with ten SWAs of various sizes, terminated to the top surface, running vertically down to their respective fuses. (from 50mm up to 150mm 4 core)
There are both Neutral and earth busbars running down the side, and along the bottom, of the chamber.
The earth busbar is, at regular intervals, bolted to the chassis. The neutral is bolted to the earth, through insulating spacers.
If I clamp the earth busbar where I can get the jaws around it, I can read a maximum of 28A returning current - I can clamp around two of the supports for the busbar - each one has in excess of 3A flowing between the busbar and chassis.
I cannot clamp around all of the individual earth cables which attach to the busbar (due to proximity to other cables).
I cannot isolate ANY of the outgoing circuits.
I did manage to clamp the supply cables (including neutral), and found 2 with approx 5A each "missing".
This still leaves me with around 18A (at least) unaccounted for.
Thoughts / suggestions would be appreciated ...........:coffeeheadbang