When MK's technical department were asked if a double socket was rated at 13A or 26A they answered as follows:
MK state that when they product test their double sockets they apply 100% of full load to one socket and 50% to the other. ie They use 20A to test the double socket but only for their inhouse product quality control.
They also say that you may plug in two loads that bring the total load on that double socket to above 13A but a diversity factor must be part of that. Continous loads of greater than 13A would damage the socket.
When asked 'could two 3kW boilers could be 'theoreticaly' be plugged into a double 13A socket?' I was told no, the socket cannot handle that load as there would be no diversity present if both were turned on at the same time.
*
MK state that when they product test their double sockets they apply 100% of full load to one socket and 50% to the other. ie They use 20A to test the double socket but only for their inhouse product quality control.
They also say that you may plug in two loads that bring the total load on that double socket to above 13A but a diversity factor must be part of that. Continous loads of greater than 13A would damage the socket.
When asked 'could two 3kW boilers could be 'theoreticaly' be plugged into a double 13A socket?' I was told no, the socket cannot handle that load as there would be no diversity present if both were turned on at the same time.
*