Pits

Junior Member
Joined
May 27, 2011
Messages
9
Reaction score
0
Have just installed 20 external LED spike lights that the client has supplied. All wiring is SWA and on an 10a 30ma RCBO. All was well for a while!

Called back at tripping occurring. Found that the Gardener damaged the SWA and a flex from wiska box to fitting. We returned to repair but after a few hours breaker tripped again and so it continued.

Returned after a rethink. Tested fittings and found insulation resistance on the flexes varied from poor to very poor. Stripped on of the flexes so just single insulted cores and resistance excellent as you would expect (seeing as air has a high resistance)

Anyone had anything like this before?

 
Last edited by a moderator:
Have just installed 20 external LED spike lights that the client has supplied. All wiring is SWA and on an 10a 30ma RCBO. All was well for a while!

Called back at tripping occurring. Found that the Gardener damaged the SWA and a flex from wiska box to fitting. We returned to repair but after a few hours breaker tripped again and so it continued.

Returned after a rethink. Tested fittings and found insulation resistance on the flexes varied from poor to very poor. Stripped on of the flexes so just single insulted cores and resistance excellent as you would expect (seeing as air has a high resistance)

Anyone had anything like this before?

Not exactly sure what the question is you are asking...??

is it either....

1/ Has anyone ever seen a cable damaged by a gardener ?

or..

2/ Has anyone ever seen an IR tester that can show levels low enough that cause a 30ma RCD to trip? 

i.e. give test results in Kilohm's not Megohms?

most IR testers I have seen give Megohm readings to two decimal places...

e.g.  0.00Meg..    (don't forget 1Megohm = 1,000,000ohms)

and   9.999kilohm's  (or 9,999ohms)   would show as 0.00Meg

BUT  9000Ohms is to high to cause a 30ma RCD to trip!

230v / 30ma = 7666.66Ohms  or 7.66K

3/ So is the question has anyone ever come across someone not to clear about the actual test results they are getting?

or

4/ Has anyone ever seen someone not do the dead tests on the cable first before enegising it...

as surely if the cable had been correctly tested you wouldn't have your "low" readings...?

(What are the actual readings of the tests you have taken?? )

If its one of those four questions then my answers would be:-

1/ yes

2/ no, to read levels this low I use a low ohms continuity scale on a suitable tester.  

3/ yes

4/ yes

Unless its a different question and you can provide a bit more info......

:popcorn

 
We have found external spike lights that pull moisture up through the flex and gland causing condensation in the fitting that builds up over time.

This country is not designed for the imported so called garden lights if you ask me.

We now fit Hunza lights which have worked much better, but still no faith in UK garden lighting products.

 