I had an interesting EICR rush job today, the report had to be supplied as soon as the testing was carried out.
I gave an unsatisfactory result, as there were many C2 codes given, however I thought it may be a useful exercise if I posted the findings here and let people have a say.
The test was carried out on a Victorian house and the supply was TNS. I suspected due to some very old MK plug type fused spurs that the property was rewired probably early 1960's.
A new meter was fitted, and supply from the HED to meter was 25mm from the meter to DB 16mm tails and 6mm main earth.The properties main fuse carrier was unmarked and although I suspect a BS 1361 this was not verified.
There was no gas bonding and no water bonding. Before the DB was a 63 amp 0.1A BS 4293 in an enclosure.
The distribution board was an old wylex rewirable fuses with 6 circuits. 5 of these circuits were wired in Vulcanised Rubber.
Insulation tests on the vulcanised rubber;
Cooker = >500 M hms
Sockets = L-E 273 L-N 257 N-E 244 M hms
Lighting = 2.08 M hms
R1=R2 on sockets =0.93 Zs = 1.08
Ze = 0.79
The lighting circuits had no earth present and all the switch plate back boxes had plastic lugs, all the lights with the exception of the kitchen light were 1960's type bakolites with glass domes and porcelain lamp holders.
The immersion heater was wired to a fuse spur in the kitchen and terminated at exit into a 30 amp junction box with flex to the immersion heater. This heater was situated at the rear with no access to test.
Now I have given a few examples and some of the above were C2's.
I would like to see if anyone can give me a C2 that is not quite as obvious from the details above. The information is there. Do not worry it is not a test, and I acknowledge that people code differently.
I gave an unsatisfactory result, as there were many C2 codes given, however I thought it may be a useful exercise if I posted the findings here and let people have a say.
The test was carried out on a Victorian house and the supply was TNS. I suspected due to some very old MK plug type fused spurs that the property was rewired probably early 1960's.
A new meter was fitted, and supply from the HED to meter was 25mm from the meter to DB 16mm tails and 6mm main earth.The properties main fuse carrier was unmarked and although I suspect a BS 1361 this was not verified.
There was no gas bonding and no water bonding. Before the DB was a 63 amp 0.1A BS 4293 in an enclosure.
The distribution board was an old wylex rewirable fuses with 6 circuits. 5 of these circuits were wired in Vulcanised Rubber.
Insulation tests on the vulcanised rubber;
Cooker = >500 M hms
Sockets = L-E 273 L-N 257 N-E 244 M hms
Lighting = 2.08 M hms
R1=R2 on sockets =0.93 Zs = 1.08
Ze = 0.79
The lighting circuits had no earth present and all the switch plate back boxes had plastic lugs, all the lights with the exception of the kitchen light were 1960's type bakolites with glass domes and porcelain lamp holders.
The immersion heater was wired to a fuse spur in the kitchen and terminated at exit into a 30 amp junction box with flex to the immersion heater. This heater was situated at the rear with no access to test.
Now I have given a few examples and some of the above were C2's.
I would like to see if anyone can give me a C2 that is not quite as obvious from the details above. The information is there. Do not worry it is not a test, and I acknowledge that people code differently.