The electrician went through the wall behind a double socket. He split the ring and took it round the conservatory. I am proposing to reinstate the original ring by putting a double pole switch in place of the socket and reconnecting the conservatory on the switched side.
As the others have cautioned this task is not a simple swapping an accessory over task. You will need a test meter to verify the correct legs of the ring and the continuity of the ring. Also don't assume the original was wired correctly, Many of us have seen wiring where rings have been crossed or have legs broken. All cable ends need testing and verifying before you reconnect them. I am also interested how you are proposing to take off a double socket and replace it with a double pole Fused Connection unit. You will need to modify the back box as well. Can be tricky if its currently flush into wall. Surface box shouldn't be too hard. It may be easier to identify if you have a mix of red/black and blue/brown cables between the house and conservatory. It reminds me of that bit in the film Apollo 13, 'Gentlemen we need to make this fit into the hole for this'.I would like to reinstate the original ring and have the conservatory wiring on a switched connection that is compliant. Is this possible?
Is there such a thing as a switched fused spur which is double pole? Perhaps they all are DP, I don't know.