brummydave
Anyone had this before?
Called to investigate nuisance tripping - i'll get to the RCD stats later - and customer's main suspect was conservatory electrics "after all the recent storms and rain".
Checked out wiring, socket, outside lights and inside ceiling fan/light. Found no damage, short circuits or corrosion. Loop impedance was good (0.87Ohm) and IR readings nearly all >500MOhm. Until I came to the feed from light switches to the inside fan/light.
I got low IR readings of 2MOhm Neutral to Earth.
So I took down the dead-wasp-infested fan unit and tested the wiring again - IR all back up to >500. Suspect unit I thought. Removed the three 60w tungsten lamps (lightbulbs to all customers of course) and tested again. IR at >500.
Inserting one lamp gave an IR of about 18MOhm, having a second made it 11MOhm, and the third took it down to 5MOhm.
Replacing them all with new 60W tungsten lamps - ths customer has a shedload and doesn't like anything else - and my IR readings were all >500MOhm.
I was glad to get that mystery sorted, but never have I heard of this before in a lamp. After replacing heater elements where insulation has broken down I should've suspected the lamp earlier as it's effectively a heater!
Hopefully the nuisance tripping will have ceased. Although with RCD readings like these I think it may be hypersensitive rather than 'in-spec':
Time (0deg and 180deg)
x1: 11.7ms and 20.1ms
x5: 7.8ms and 17.6ms
Current:
15mA and 24mA
Comments and thoughts appreciated.
Current:
15mA and 24mA