Now are you sure you meant 'earth' them - or are you thinking they require 'bonding'. :^O
main earth bond or supplementary earth bonding?
I'm having second thoughts myself now - metal pipe........in the building........within the 'equipotential zone'..........hmmm - I've got a 4 foot length of copper pipe lying in the hall, better go and 'bond' it........ oh no, hang on......it's NOT EXTRANEOUS!!!!
Anyway, back on topic......
GS,
Take a resistance measurement between the offending pipe and the MET.
If your reading is
bigger than 22 K ohms, then you can consider it
not extraneous, and not bother bonding.
This would be the proof that Steptoe BS7671 requires.