Max demand
Am I right is thinking if I wanted to work out the max demand of an install the following would be a good rule of thumb.
40 A - cooker
32A - ring
32A - ring
6A - lights
20A - radial
32A - ring
6A - lights
6A - smoke
40 + (0.4 x 32+32+6 + 20 + 32 + 6 + 6 ) = 93.6A
I understand that there are rules to diversity in BS7671 depending upon the type of circuit but is the above calculation an accepted method ?
But I also guess that if you turned on a fair amount of the appliances and put a clamp meter round the tails , this is also an acceptable method to work out max demand ?