No I'm not calling volt drop Zs so ner
.
If you comply with volt drop, earth loop impedence for circuit is met which is what I was getting at albeit not clearly.
Sorry mate, but that is incorrect.
volt drop measures the resistances of the particular conductor size, over a given length, for a given current travelling through it.
i.e. the resistance of the neutral and phase conductors (on a single phase system).
The earth loop, (Zs, as you mentioned), is the resistance measurement of:
The phase conductor to the CU.
Supply phase to the transformer
Transformer resistance.
(TN-S) - Cable sheath back to MET.
(TN-C-S) - Supply PEN to HED
(TT) Transformer earth spike, general mass of earth, earth rod.
Earthing conductor.
CPC to point of test.
You CANNOT guarantee a circuit will pass max Zs by measuring the resistance of the phase and neutral cores of the final circuit!
or am I going totally loopy????