Metal Consumer Units ?

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

Evans Electric

TEF LINUX ADMIN™
Supporting Member
Joined
Sep 15, 2008
Messages
23,507
Reaction score
527
Location
Birmingham
Just looking at Reg ;   421.1.201  which says  ...............  Consumer units in domestic ( Household) premises have to be metal .

So , plastic ones can still be used in premises other than domestic (Household) .   I assume . :C

 Changing one in a solicitor's office shortly , which is a commercial premises ..I'm using plastic anyway but after 2016  it would still be plastic as its not a domestic household.

There are many premises which are not domestic (Household)   Reg. states it quite clearly.

Also just thinking ...why the hell didn't they tackle the cause of the overheating  , as in loose terminals by inadequatly trained operatives ,  consumer units do not burst into flames just because they are made of plastic .....they used to be made of wood FFS !!!!    at one time .  

Fires in consumers are caused by overloading & loose terminal screws  ...oh and respected manufacturers having their products made cheaply by people who produce inferior goods by using cheapo materials & parts.

The fact that the case is made of plastic has no bearing on the matter whatsoever .

 
And dave from the pub will still buy a plastic cu from the big shed and install it in a house at the weekend for cash.

This reg IS a farce and we sparks need to continue to voice our views until the 31st Dec '15

The regs should recommend better built cu's and/or smoke alarms in the same room as the cu. A metal CU is nothing more than a sticky plaster over a bigger problem

 
Just looking at Reg ;   421.1.201  which says  ...............  Consumer units in domestic ( Household) premises have to be metal .

So , plastic ones can still be used in premises other than domestic (Household) .   I assume . :C

 Changing one in a solicitor's office shortly , which is a commercial premises ..I'm using plastic anyway but after 2016  it would still be plastic as its not a domestic household.

There are many premises which are not domestic (Household)   Reg. states it quite clearly.

Also just thinking ...why the hell didn't they tackle the cause of the overheating  , as in loose terminals by inadequatly trained operatives ,  consumer units do not burst into flames just because they are made of plastic .....they used to be made of wood FFS !!!!    at one time .  

Fires in consumers are caused by overloading & loose terminal screws  ...oh and respected manufacturers having their products made cheaply by people who produce inferior goods by using cheapo materials & parts.

The fact that the case is made of plastic has no bearing on the matter whatsoever .
I have said the same on this forum a few times

I also asked the same questions on the Webinar....all questions were ignored

"Why not eliminate the cause of the fires ....shite workmanship,,shite training, shite products...instead of keeping it in a metal box"

 
Okay, devil's advocate.

BS7671 is not a legally binging set of "requirements"

So what would be the penalty of fitting a plastic CU after 1st Jan 2016?

I guess nothing....... Until it catches fire?

I still don't see many metal ones for sale yet. My guess is there will still be big stocks and platic ones will still be widely on sale after Jan 1st.

 
Last edited by a moderator:
I've fitted a couple of metal CU's in the last week or so,,, Schnider ones, they're not too bad however they are much heavier than the plastic ones and the knockouts to the rear are a little small.... I think I'm going to have to buy a pair of nibblers

 
Yesterday, I posted the comments below on the NAPIT Forum, in response to opinions about EICR coding of plastic boxes after 01/01/2016.

Quite a few people agree with my point on screw torques, judging by the good sales of my Torque Screwdrivers. Thanks guys!!

"IMHO, if the original plastic CU, as installed, complied with BSEN60439-3 or BSEN61439-3 and was installed in accordance with the manufacturer's instructions and is still in good serviceable condition, then the only issue is compliance with 421.2.201, with regard to "non-combustible material"
Since this will not be the case, OSG G3.5 advises us to check for correct torque settings of terminal screws, check for evidence of overheating and check that all original components of the CU are in place, to safeguard its ongoing use.
This surely means FURTHER INVESTIGATION, which is code F1.
This would be recorded on an EICR and this investigative and possibly remedial work would have been undertaken for an EIC.
The key issue, IMO and the opinion of LFB and others is correct torque settings for the screws. This would minimise connection overheating and provide a measure of defence within the EAW Regs, in the event of litigation."

DaveS on NAPIT Forum

aka SBS Dave

 
I admit to picking up on Kerch's previous posts, just adding my threepen'th. :Salute

On a similar vein , I emailed NICEIC/ELECSA  a week ago ,commenting on an article in their "Connections"  magazine which seemed to infer that " Legal action would be taken against members who are found not to be applying the new Regs. "

I felt that "The Electric Police"  had finaly been issued uniforms & batons & would be hitting the streets shortly.

I phoned to ask about my unanswered email ... spoke to a nice lady there who assured me that it was an unfortunate turn of phrase in the article and referred to  possible , third parties taking action but not NICEIC/ELECSA.

I was also pleased to hear that I was not alone with the complaint ,  others from the brotherhood had risen to voice their concern.

 
It boils down too, it's easier to implement something new than to admit that the training is inadequate, as that's an admission that they got it wrong whereas if we fail to follow the new introduction then we got it wrong!!

Laymans english: pass the buck!

 
It boils down too, it's easier to implement something new than to admit that the training is inadequate, as that's an admission that they got it wrong whereas if we fail to follow the new introduction then we got it wrong!!

Laymans english: pass the buck!
But thats not all of it. Its RUBBISH parts and poor workman ship - often installed by un trained people!

 
how many loose burnt out terminals have you seen on an old wylex wooden board with 2 proper screws on the cable compared to newer stuff?
None and it breaks my heart ripping them out. Decent qualilty, well built and have lasted for decades - unlike the shyte produced these days.

 
how many loose burnt out terminals have you seen on an old wylex wooden board with 2 proper screws on the cable compared to newer stuff?
2 screws per connection was a bloody good idea. So simple.

How long before we are not allowed to screw CU's to a wooden back board?  The fire contained inside a tin box could get so hot as to ignite the wooden back board.....

 
2 screws per connection was a bloody good idea. So simple.

How long before we are not allowed to screw CU's to a wooden back board?  The fire contained inside a tin box could get so hot as to ignite the wooden back board.....

and what about the big hole the cables go through into the cavity???

This reg change is such an ill thought it shambles!

 
Erm....ummm....  OK  Sort out the stable door before the bunch of tw@ts have bolted on horseback ......  :C

I shall be fitting plastic consumers until  ...allowing 4 hrs on average for a domestic board ..... 8 pm on Dec 31st  but won't switch it on until 1 minute past midnight .just for the hell of it .     The Electric Police will be too busy celebrating New Year's Eve to catch me .     That'll teach 'em .

 
In my mind torque settings are only really useful if everything else is a known constant, therefore they make sense for the head on your car engine, or an MCCB into a panel board. But for a cage clamp which could be tightening down on varying numbers of stranded or non stranded conductors, I cant see how a set figure can be best for all situations.

I reckon if I got a main switch from one of the major names, a piece of 25mm tail, stripped it and terminated to recommended torque. With a bit of wiggling it would pull out! I could then get another bit of 25mm, strip it, flatten out the strands, terminate with large flat driver until I think its tight, give it a wiggle and re-tighten. Then go back to it after testing before putting cover on and give it another tweak and it'll be sound.

A torque driver is no guarentee of a good connection especially where cage clamps and 7 strand tails are concerned!

I'm not berating SBS dave, he is after-all only supplying what the market has come to demand but I cant help but feel the whole idea of torquing terminals up to a given figure is funamentally flawed

 
Top