Been reading the ESC Best Practice Guide on Domestic CU changes and thought id copy some of it out for newbies doing board changes.
Although I always fully test every circuit individually as im quite new heres what the BPG says which I think some newbies may be interested in.
10.2 In addition, as a minimum, the following tests should be carried out to the existing circuits connected to the replacement consumer unit.
- A continuity test of the protective conductor of each circuit, to the point of the accessory electrically furthest from the consumer unit and to each accessible exposed-conductive part.
-A continuity test of all ring final circuit conductors
-A measurement of the combined insulation resistance of all the circuits. The measurement need only be made between the line and neutral connected together and the protective conductor connected to the earthing arrangement.
-A test of polarity and a test to establish earth fault loop impedance (Zs) at each accessible socket outlet and at least one point or accessory in every other circuit, preferably the point or accessory electrically furthest from the consumer unit.
-RCD Tests
10.3 The EIC should identify in the comments section any potential dangers that exist with the reconnected circuits and other defects that exist in the reconnected circuits , and that the installation of the consumer unit has been carried out in accordance with the recommendations in this guide.
Hope this helps someone.
CheersGuinness
Been reading the ESC Best Practice Guide on Domestic CU changes and thought id copy some of it out for newbies doing board changes.
Although I always fully test every circuit individually as im quite new heres what the BPG says which I think some newbies may be interested in.
10.2 In addition, as a minimum, the following tests should be carried out to the existing circuits connected to the replacement consumer unit.
- A continuity test of the protective conductor of each circuit, to the point of the accessory electrically furthest from the consumer unit and to each accessible exposed-conductive part.
-A continuity test of all ring final circuit conductors
-A measurement of the combined insulation resistance of all the circuits. The measurement need only be made between the line and neutral connected together and the protective conductor connected to the earthing arrangement.
-A test of polarity and a test to establish earth fault loop impedance (Zs) at each accessible socket outlet and at least one point or accessory in every other circuit, preferably the point or accessory electrically furthest from the consumer unit.
-RCD Tests
10.3 The EIC should identify in the comments section any potential dangers that exist with the reconnected circuits and other defects that exist in the reconnected circuits , and that the installation of the consumer unit has been carried out in accordance with the recommendations in this guide.
Hope this helps someone.