Hi all,Yes, i know what you are saying, and it IS a difficult area filled with contradictions, but an EICR inspection is a LOT different from initial verification, when you ARE looking to see that all complies with the current regs.
With an EICR i would contend that you are looking for signs of deterioration and damage, and that it was correctly installed in the first place.
The "model" forms state "The inspection and testing detailed in this report and accompanying schedules have been carried out in accordance with BS 7671: 2008 (IET Wiring Regulations) as amended to"...
I would contend that this means that the testing has been carried out as required by the bit of the regs concerning periodic testing, [which is completely different from initial verification] which is concerned with seeing that a NEW installation complies with the current regs.
For a start off, on an EICR you can have "sampling" and also "limitations" which you cannot have on an initial verification. Obviously you cannot knock half the building down to inspect concealed items, and there are times when you cannot do tests required in an initial verification purely because you cannot turn the power off!!
The model forms go on to state;
"This Report should only be used for reporting on the condition of an existing electrical installation. An installation which was designed to an earlier edition of the Regulations and which does not fully comply with the current edition is not necessarily unsafe for continued use, or requires upgrading. Only damage, deterioration, defects, dangerous conditions and non-compliance with the requirements of the Regulations, which may give rise to danger, should be recorded"
Soooooo, the bit i highlighted in blue above, pretty much rules out C1 and C2 for no rcd, in an installation designed before these things were required, so i would give it a C3 improvement recommended...
What say you all??
P.S. Sorry if i sounded a bit rude in my earlier post, i was in a rush and typed it out at full speed!!! Reading it again, it does sound a bit, well, i suppose the word i was going to use would be blocked, but not very polite or constructive!!!!!!
Sorry all!!
john...