Hang on, we are talking about an installation indoors, inside the Faraday Cage, we do not know what will happen outside it could be nothing or it could be every appliance made out there, that's why we must assess each and every installation we are involved with.We are carrying EICR and the last two letters Condition Report, we are not the Electrical Police.
The installation must be safe for continued service, your report is based upon the latest version of BS 7671 which has identified the increased risk of electric shock outdoors.
I'm not concerned with outdoors, unless I have supplied out there, I will advise the client if they have no RCD protection and they intend to use appliances outside then they need to have some form of RCD protection be it at fuseboard, socket or plug.
Id suggest you code it as a 2, if anything happens it will be your A**e on the line.
Indoors if its likely to become live it should be bonded, if it's all plastic then no need, again each job is different to the next.
If its extraneous, you bond it.
Is the RCD secondary protection or primary, all makes a difference.
The point is this, you code 1,2,3 based on the latest edition, the touch voltage curve for outside would be L2 as it would be for a bathroom hence the 50V requirement.
So if you code a lack of Main bonding or a bathroom with no Supplementary bonding where its required you would code a 2, as i have pointed out, the risk is higher or equivalent outside than the two instances mentioned.
So if sockets are potentially going to be used for outdoor equipment then if you code the above as a 2 then you must code no RCD as a 2, the potential risk is the same, how can it be a 3.
If you pass that installation and someone receives a fatal electric shock who's going to get the blame, I really don't see retrospect as a defence.The new Regs recognise the risk outdoors and require RCD's, you should know of the increased risk and you need report the risk.