Installed a 16a radial on a 16th edition split load Hager c/u.
S type RCD main switch and one side 30ma RCD, all circuits protected by 30ma RCD except 2x 6a lighting circuits.
These are the results I got:
PFC L/N 1.60ka L/E 8a
ZE/RA 239 ohms
R1+R2 0.20 ohms
ZS by calculation 239.20 ohms
RCD 1x 34.0ms 5X 16.0ms
My concern is (unless I've done something wrong somewhere) that a ZE/RA over 200 ohms is considered unstable and what should be done to rectify. I'm aware the high ZS on the new circuit is covered by the 30ma RCD but what about the 2x lighting circuits that are not, are they covered by the S type RCD or should i put them on the 30ma or should I just leave them as they were already like that....
Sorry for the long winded post, not much experience on TT systems, just wanna make sure all is ok (or not).
B.
S type RCD main switch and one side 30ma RCD, all circuits protected by 30ma RCD except 2x 6a lighting circuits.
These are the results I got:
PFC L/N 1.60ka L/E 8a
ZE/RA 239 ohms
R1+R2 0.20 ohms
ZS by calculation 239.20 ohms
RCD 1x 34.0ms 5X 16.0ms
My concern is (unless I've done something wrong somewhere) that a ZE/RA over 200 ohms is considered unstable and what should be done to rectify. I'm aware the high ZS on the new circuit is covered by the 30ma RCD but what about the 2x lighting circuits that are not, are they covered by the S type RCD or should i put them on the 30ma or should I just leave them as they were already like that....