A while ago now, i fitted a number of thorn piaza outside lights which were all on the same circuit. The ones i replaced kept blowing their ballasts, but it was a right pain in the rear finding out which one had blown as they were all covered over in a cage as well. And if one had gone it would knock all the others off. The MCB could not be reset until the faulty one was found. So when i replaced them i relaced all the terminals with ones with fuse holders. Much easier to find the culprit and the others would still remain working.