Right see if you can see what the issues were with the periodic test inspection undertaken this year by another electrician.
The photos are from the subsequent visit by me to undertake an EICR for the purchasers of the property, as they were concerned about the report handed over by the vendors solicitor...............the purchasers know a qualified sparks who took a look at the emailed report :innocent
The other electricians report
These are a couple of pictures I took.
The supply
The new cu fitted a month ago ............... cash job by the same fella, so no certs apart from the periodic paperwork.
Inside the cu
on one of the 32amp ring final mcb's you might just make out an additiona 1.5mm conductor.
Something missing here but not on the report issued
The fella should be ashamed for taking £200 off the woman.................she has been made aware of her error in getting a cheap cack job.
The photos are from the subsequent visit by me to undertake an EICR for the purchasers of the property, as they were concerned about the report handed over by the vendors solicitor...............the purchasers know a qualified sparks who took a look at the emailed report :innocent
The other electricians report
These are a couple of pictures I took.
The supply
The new cu fitted a month ago ............... cash job by the same fella, so no certs apart from the periodic paperwork.
Inside the cu
on one of the 32amp ring final mcb's you might just make out an additiona 1.5mm conductor.
Something missing here but not on the report issued
The fella should be ashamed for taking £200 off the woman.................she has been made aware of her error in getting a cheap cack job.