[SIZE=11pt]CIBSE Lighting Guide 12: Emergency lighting design guide section 6.3.3 Manual test devices states the following:[/SIZE]
[SIZE=11pt]...'Manual test devices should initiate the emergency changeover circuit and activate the lamp from the battery. The arrangements should be adequate and appropriate for the application'...[/SIZE]
[SIZE=11pt]Following that the statutory document BS 5266-1:2011 section 8.3.3 Test facility, states the following:[/SIZE]
[SIZE=11pt]...'Each emergency lighting system should have suitable means for simulating failure of the normal supply for test purposes (i.e. without interruption of the normal supply).'... read: turn permanent live off with the key-switch instead isolating the DB or MCB[/SIZE]
[SIZE=11pt]Also[/SIZE]
[SIZE=11pt]BS 5266-1:2011 Figure F.3 Model completion certificate – Installation – Declaration of conformity, Recommendations:[/SIZE]
[SIZE=11pt]IN9 The system has suitable and appropriate testing facilities for the specific site ( by the way referenced as 9.3.3 - that's old reference from BS 5266-1:2005)[/SIZE]
[SIZE=11pt]Following this thread when you finish your installation you must test the lighting levels and using the test facility provided (how would you test the EM lux levels with standard lighting ON[/SIZE]
[SIZE=11pt]Reference BS 5266-1:2011 Annex B:[/SIZE]
[SIZE=11pt]...'All site test work needs to be carried out by simulating a failure of the normal electrical supply and, where practicable, by using the test facilities provided'...[/SIZE]
[SIZE=11pt]Summary[/SIZE]
[SIZE=11pt]I cannot see anywhere in the British or European standards requirements to maintain the standard lighting ON while operating 'Test facility switch' or statement that would say ...' Operation of the emergency lighting test switch should not affect the normal lighting'...[/SIZE]
[SIZE=11pt]As long as the system has suitable and appropriate testing facilities for the specific site its compliant...[/SIZE]
[SIZE=11pt]Do you agree? If not can you provide some back up legal requirements, rather than just short statement ...[/SIZE]
[SIZE=11pt]...'Manual test devices should initiate the emergency changeover circuit and activate the lamp from the battery. The arrangements should be adequate and appropriate for the application'...[/SIZE]
[SIZE=11pt]Following that the statutory document BS 5266-1:2011 section 8.3.3 Test facility, states the following:[/SIZE]
[SIZE=11pt]...'Each emergency lighting system should have suitable means for simulating failure of the normal supply for test purposes (i.e. without interruption of the normal supply).'... read: turn permanent live off with the key-switch instead isolating the DB or MCB[/SIZE]
[SIZE=11pt]Also[/SIZE]
[SIZE=11pt]BS 5266-1:2011 Figure F.3 Model completion certificate – Installation – Declaration of conformity, Recommendations:[/SIZE]
[SIZE=11pt]IN9 The system has suitable and appropriate testing facilities for the specific site ( by the way referenced as 9.3.3 - that's old reference from BS 5266-1:2005)[/SIZE]
[SIZE=11pt]Following this thread when you finish your installation you must test the lighting levels and using the test facility provided (how would you test the EM lux levels with standard lighting ON[/SIZE]
[SIZE=11pt]Reference BS 5266-1:2011 Annex B:[/SIZE]
[SIZE=11pt]...'All site test work needs to be carried out by simulating a failure of the normal electrical supply and, where practicable, by using the test facilities provided'...[/SIZE]
[SIZE=11pt]Summary[/SIZE]
[SIZE=11pt]I cannot see anywhere in the British or European standards requirements to maintain the standard lighting ON while operating 'Test facility switch' or statement that would say ...' Operation of the emergency lighting test switch should not affect the normal lighting'...[/SIZE]
[SIZE=11pt]As long as the system has suitable and appropriate testing facilities for the specific site its compliant...[/SIZE]
[SIZE=11pt]Do you agree? If not can you provide some back up legal requirements, rather than just short statement ...[/SIZE]