Hi Guys,
Just done a EICR on a domestic property. Its about 10-15years old so alls good wiring wise. The only observations are that its a 16th edition board so lighting circuits with cables buried in walls less then 50mm not rcd protected. Guessing this would be Code 3? However there is no supplementary bonding in the bathroom either so would that be a code 2 for the lighting?
Thanks
Just done a EICR on a domestic property. Its about 10-15years old so alls good wiring wise. The only observations are that its a 16th edition board so lighting circuits with cables buried in walls less then 50mm not rcd protected. Guessing this would be Code 3? However there is no supplementary bonding in the bathroom either so would that be a code 2 for the lighting?