Evening All
Can someone pls clarify the test procedures for the above tests as I have witnessed various methods of obtaining this result and some very high readings logged on test sheets..
test kit is a megger 1552 , my understanding and testing method is
PEFC , 1 probe on L1 and 1 to earth , repeat with l2 to earth and L3 to earth and record the highest as your PEFC reading.
PSCC , 1 probe to L1 and 1 to Neutral , repeat with L2 to N and L3 to N and double the highest reading , whichever is the highest out of the PEFC and the PSCC is recorded as your result..
I have known people to double the PEFC but surely you only double the PSCC ???
What are your thoughts and methods ?