ill come back after kettle boils thanksYou have a response from SL (coming)...don't go yet..!!
I would concur with those thoughts Ext15Could it be the earth is simply missing?... (Is there provision at the HED for the earth?)
Can't see why you would need to open anything up to identify if it is P.M.E.?i havent opened it up as yet can,t remember if it is sealed or not
agree about label(nothing there ) cabel entering head is insulated so there is no clamp for tns so i dont think this is awolI would concur with those thoughts Ext15Can't see why you would need to open anything up to identify if it is P.M.E.?
The earth connection bit is normally accessible to the side of the main fuse cut-out, typically with one or two nice big screw terminal connection positions?
Ignore your readings for now...
just identify the physical incoming supply connections..
Also I have always been under the impression that PME (TN-C-S) supply's,
have to have a durable warning label fixed very near the supply fuse with words something like "P.M.E. SYSTEM" engraved into it.
I think most of the ones I have come across do anyway?
Are you sure its not a TN-S with the earth gone AWOL?
To do your Ze you should have isolated all bonding so you only read through the supply earth. :| ?:|
your quick Zs at a socket (100ohm) could be a bad socket connection, or something else on that circuit maybe?
Spooky! 'welcome to the twilight zone'....agree about label(nothing there ) cabel entering head is insulated so there is no clamp for tns so i dont think this is awolhavent done ze yet as inspection did not prove there to be an earth, iknow this may sound daft but in my defence i will do this when i upgrade board at that time I always tend to think if i cant see something it is not there but i take on board your segesstions do you have any more?
Spose it could be TT with a stake been buried or lost over the years..one house is pme the other as far as i can see is tt but i cant find an earth stake outside.
Now, forgive me for being daft guys:If I have a TT where I can`t get a good reading; or physically demented issue to send in a rod, I`ll ask DNO for PME. If available(usually is!), they do it for about
Although we SHOULDN`T assume anything (assome makes an ass of u and me!), Due to the nature of this forum we must, sometimes, assume certain things.can we assume this house is within distance for DNO to provide a PME system tho?
Absolutely NO CHANCE!!! X(Now, forgive me for being daft guys:
sad? yep thats ok!:OOh:Oer....okay.?
Nobody told me that one. :_| :_| X(
sad, dejected, unloved, and sitting in the corner with a poodie
Could be concentric old cable on insulators under soffit has been joined to newer cable which enters house.is it a concentric cable?is the 1st house really PME or has some1 just opened the cutout and linked it?
is there any good reason you couldnt TT the house anyway?
DONT like PME,
its big gurls earthing, LOL.
does seem strange tho that 2 houses next to each other are different.
thats what really makes me wonder about part 1, and if 2nd house is water main earth only!!!!
please see reply i sent to steptoes post.Spooky! 'welcome to the twilight zone'.... The earth that isn't there?
how old is the property?
I have had a TT job where the original earth rod had be buried under 4inches of tarmac on a driveway down the side of the property.
and I've had another where the earth rod was suck in the ground...
below an internal floor.. :_|
lift the boards.. and there was me rod!
Looks like you need to go on a thorough "Rod Hunt"! follow every bit of yellow/Green wire you find.. see where it goes to??
Just seems very strange two properties next door to each other? :|
Are the both the same sort of age.. or was one a later addition to the street? :|