What sort of voltage indicator are we talking about that shows earth leakage?Thank you very much for time and detail that you have put in to your response. I initially missed the IR test between L-E and N-E and went back today and did that. I found no reading between L-E?
The second query I have is that I went to look at a metal single light switch which is occasionally giving a electric shock, I couldn't find any problems: the earth was proper/all connections were correct, the only thing was that when I put the voltage indicator on the outer metal plate it buzzed and showed earth leakage. Please advise.
Thank you
You are saying L-N and N-E is reading 299 Megohms so this is clear but then say L-N very low reading which to me is a near short. You are not making sense are you competent to be doing the tests?I'm using megger 1551 tester and L-N and N-E have readinf 299 M ohms. but L-N very low reading.
Whats your very low L-N reading?I'm using megger 1551 tester and L-N and N-E have readinf 299 M ohms. but L-N very low reading.
Definitive answer required or check tomorrow what your L-E reading is then come back and let us know.normal voltage indicator. But I checked other front plate that doesn't buzz, why is that?
So are you using a two pole voltage tester or a non contact voltstick?
cooker is not connected. test meter didn't showed any reading L-E.
normal voltage indicator. But I checked other front plate that doesn't buzz, why is that?
cooker is not connected. test meter didn't showed any reading L-E.
Takes these with you guaranted a BUZZ.