Hi guys! I've got an electric shower to replace. The new one is 9kW/230. The current circuit is 10mm with no RCD protection - old Wylex DB with plug in breakers. Is it ok to come off from the 45A breaker and to put 40A RCD in enclosure.

Thanks

 
Specsyour too kind,,,,,to kind
You are only creeping cuz you know the beer is getting low in KME's fridge..

and I have four bottles stashed next to be bed that I nicked of CanoeyKayak when he was not allowed to drink!!!

:p

GuinnessGuinnessGuinnessGuinness

:Blushing

:coat

 
1 major problem I have with this,you are proposing to protect a 40A RCD with a 45A OCPD.?!

can we think about this for a moment please.
well spotted! :Applaud

Only just noticed that in the OP...

but I did suggest a 63A RCD meself your honour! :Salute

 
Thanks Step. I was not sure myself...9000/230=39.16A. Would be 40A breaker sufficient?

 
its the simple rule phase,

load<OCPD<cable

except you have now inserted another device, which is required to (in your instance) to slot between the cable and OCPD positions,

load<OCPD<RCD<cable

40A MCB or 63A RCD, and TBH, no real difference in price between 40 or 63A RCDs IMO.

HTH

 
I see you point step. Can I put the RCD after OCPD. I was going to come off from the DB and put the RCD between the OCPD and the shower.

 
Thank you guys for all your helpfull replies. Proper enclosure really does make big difference.

 
I would not do this as I think it would exceed (might) the total rating of the old wylex board.

Surely Splitting the tails would be better??