- Dec 25, 2011
- 5,468
- 78
I've posted elsewhere about a new 7.3kW induction hob I have (yet to fit). It's to replace an old 6kW solid plate type. Currently supplied from a Crabtree C50 board with a Type 1 30A breaker on a 6mm T&E and the 6kW hob fed by a short length of again 6mm T&E from the ccu. The hob is made in Turkey and the English is in some places a bit lacking.
The new hob manual specifies a supply cable of 3x2.5mm HO5VV-F. So WITHOUT taking into account diversity I'm looking a a potential full load of 32A. Taking into account diversity then I get 10A + 30% of 32A (no socket btw on the ccu) which gives me 19.6A.
The 2.5mm H05 flex I have has a rating of 25A. I've taken the diversity calc from the OSG for a "cooking appliance" so in theory the 2.5mm is OK. BUT how does this sit with the regs as in surely there is always the potential with a hob (more so than an oven?) to achieve full load. So I have potentially the cable rating LOWER than the OPD.
My thoughts are to simply fit 6mm T&E from the CCU to the hob and IGNORE the manual. A bit worried though as it is not "heat resistant" like the H05. I could fit 3-core, 4mm butyl..........
Any thoughts on my thought process/the way to go would be appreciated.
Many thanks
Many thanks