Hi all,
It is "PNB", that so far as i know, stands for "protective neutral bonding" I do not really understand the difference though, but one thing i do know, is that i often read that the DNO has "converted" a supply from TNS to "PME" at the cutout, but as far as i know this is simply not possible without digging up the road outside, as PME, again, so far as i know, requires that there is an additional earth rod at the point where the service cable joins the main..
Here is something i have included from Eon just as a matter of interest:
E2.8.5.1 Provision of LV Earthing Terminal
The provision of a LV earthing terminal has been achieved by various means in the past. The
present company policy with regard to the provision of a LV earth terminal is detailed below :-
PME Terminal (TN-C-S)
All new supplies, or existing customers requesting a load increase, will normally be
offered a PME terminal. However, for reasons of safety some installations are not suitable
for a PME earth terminal in which case a TT supply will be offered (see Section E6.3 for a
detailed list of exceptions). Under the ESQC Regulations, the Company is not obliged to
offer a free PME earth terminal to existing customers that do not already have a PME
earth.
Sheath Earth Terminal (TN-S)
The Company has an ongoing obligation to maintain the integrity of the sheath earth
terminal of customers which already have this type of earthing. If an existing sheath earth
customer requests a service alteration or in the event of a fault repair then the existing
sheath earth must be maintained unless the customer request a PME earth terminal
instead. A sheath earth terminal shall not be made available to new customers (or existing
customers if they do not already have an earth terminal).
PNB Earthing
PNB is a special method of earthing, similar to PME, where the neutral earth is installed at
or adjacent to the customer