Hi All,
$park, when you talk about Rb, we all know what it is, the resistance of the rod at the transformer end, we all know what it should be, 21 ohms max, but we do not all know the "shorthand" term for it, as, like Sidewinder said, it is of no interest WHATSOEVER to a normal electrician.
So you might use MCB's in an install, so what, if it is a TT install you will HAVE [normally] to use an RCCB in addition to give earth fault protection, so as long as your loop impedance is RELIABLY low enough, that the operating current of the RCCB does not cause touch voltages to go about 50V, who cares about anything else????
If the DNO do not care about maintaining the TNS earth, what sort of response you think you going to get if you phone up and say "good afternoon, i have an Ra of 5 ohms, but i cannot get Zs below 20 ohms, so there must be something wrong with the rod at your end????"
john...
$park, when you talk about Rb, we all know what it is, the resistance of the rod at the transformer end, we all know what it should be, 21 ohms max, but we do not all know the "shorthand" term for it, as, like Sidewinder said, it is of no interest WHATSOEVER to a normal electrician.
So you might use MCB's in an install, so what, if it is a TT install you will HAVE [normally] to use an RCCB in addition to give earth fault protection, so as long as your loop impedance is RELIABLY low enough, that the operating current of the RCCB does not cause touch voltages to go about 50V, who cares about anything else????
If the DNO do not care about maintaining the TNS earth, what sort of response you think you going to get if you phone up and say "good afternoon, i have an Ra of 5 ohms, but i cannot get Zs below 20 ohms, so there must be something wrong with the rod at your end????"
john...