Overloading what? What cable is 24A rated?
Overloading the circuit is what I meant. Thinking about it, if the cooker's pulling 27A and then 13A or more is being used on the double socket, then the 30A fuse should blow. So actually it could be seen to be fine. Just feels really wrong!
Beg your pardon, i meant 27A not 24A when refering to the 2.5mm TnE.
its not a spur, its simply a radial part wired in 6mm and part wired in 2.5, with a switch at the join, and a double socket at the extreme point, think a normal lighting circuit, with the last leg to the utility room wired in 1mm, its not a spur, just a different size cable, common practice in com/ind to allow for volt drop, I wired lights in 4mm before now gradually dropping in size as permitted.
The join is not at the switch, it's at the cooker. There's a 6mm from cooker control to cooker, and then a 2.5 out the back of the cooker itself.
That's why I suggested disconnecting the 2.5 and moving it to spur out from a nearby socket.
The reg I found was 433.2. " A device for protection against overload shall be installed at the point where a reduction occurs in the value of the current capacity of the conductors of the installation"
As there isn't such a device, it was my thought to suggest the twin socket feed be moved to a better location.
But then 433.2 also says that the device can be installed on the run. So you could argue that the socket outlet is that device protecting a conductor against overload as it ensures plugs fused at a maximum of 13A will be used. But that seems much more shaky ground.
Looking at appendix 15 I can see the idea of unfused spurs on lower capacity cable but these diagrams have anomalies anyway! Fig 15B shows spurs from spurs on radials when they're using identical cable. Now that's something I thought wasn't allowed. And the diagram goes against the text saying an "unfused spur should feed one single or twin socket outlet only".
Reminds me of my latest regs course where we found many contradictions in the big green book!
Oh and the situation is more complicated as the earth continuity to the cooker control unit is diabolical! I got a r1+r2 of 70Ohms, and a Zs of over 13!
As the place is earthed through steel conduit, it makes for interesting times.