I was asked to look at a building that was supplied from another main building.
The main building has a three phase supply, and it looks like the DNO have changed the earthing arrangements from TN-S to TNC-S but thats another story.
Any way I calculated the demand for the building which has had various alterations through the years, one of which was a 10mm swa with a 45amp breaker to supply another buiding.
I calculated with diversity it comes out at around 136amps.
When I went to the source I found two cable that supplied the buiding where as follows
Power circuit 60amp 6mm MICC cable
Lighting circuit 20 amp 4mm MICC cable
Part of the cable run is underground (MICC cables love underground) :^O
I never met the customer, only the caretaker, I have asked him to get the owner to call me I think there will be some major upset when he is told he has to replace 6mm and 4mm cable for at least 35mm if not 50mm
The main building has a three phase supply, and it looks like the DNO have changed the earthing arrangements from TN-S to TNC-S but thats another story.
Any way I calculated the demand for the building which has had various alterations through the years, one of which was a 10mm swa with a 45amp breaker to supply another buiding.
I calculated with diversity it comes out at around 136amps.
When I went to the source I found two cable that supplied the buiding where as follows
Power circuit 60amp 6mm MICC cable
Lighting circuit 20 amp 4mm MICC cable
Part of the cable run is underground (MICC cables love underground) :^O
I never met the customer, only the caretaker, I have asked him to get the owner to call me I think there will be some major upset when he is told he has to replace 6mm and 4mm cable for at least 35mm if not 50mm