If you are going to have 100m A Time delay RCD AT SUPPLY END then I can see no reason why not to have ROD PERMANANT at Supply end and solve problem.Right - lets see if I can help or confuse things some more.........We`re going to need supplies for bar equip, lights and possibly musicians equipment, so I intend to supply all three phases.
I`d prefer to have 3 X SP breakers; so 1 overload doesn`t take out all circuits.
The reason I don`t want the 30mA at the commando socket by the pub is that, if a piece of bar equip, or a musicians amp has a fault, we`d lose all power, and someone would have to go from the marquee to the main building to re-energise.
I`m thinking 100mA(T) at the building (if required) ; protect the outgoing flex with the PME. Drop the earth at the portable DB, and have a seperate plug/socket to connect to the (permanent) rod. The DB could then be fitted with RCBos (thanks Sidewinder ) and everybods is happy??
Does that make things easier? I haven`t perused the BRB yet - thats tomorrow`s project.
KME