T & E Current Carring Capacity in trunking

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.
Joined
Feb 10, 2009
Messages
342
Reaction score
18
Hi.

I believe T & E irun n trunking would probably be Reference Method B?

Trouble is I can't find the correct table to determine the Current Carrying Capacity - Table 4D5 only gives reference methods 100,101,102,103,C and A.

The cable in question is 10mm and is only being run in trunking for asthetic reasons.

Any ideas please?

 
Is the cable run with any other cables in the trunking? if not just class it as a clipped cable in My opinion.AndyGuinness
No its on its own - I didnt know whether to use table 4D2A which gives 52A as opposed to method C in table 4D5 which gives 64A?

 
In the Electricians Guide to the BR's, Table 2.3.1, It gives a current rating for 70c flat thermoplastic etc cables. It lists -Inst Ref B - 10mm - 52A. and claims this to be taken from Table 4D5 of BS7671. if that helps...

 
In the Electricians Guide to the BR's, Table 2.3.1, It gives a current rating for 70c flat thermoplastic etc cables. It lists -Inst Ref B - 10mm - 52A. and claims this to be taken from Table 4D5 of BS7671. if that helps...
Thanks for this i've checked the Electricians guide Table 2.3.1 - and the figures it gives for Method B are the same as those given in BRB Table 4D2A for Method B - which is conclusive enough for me

 
Table 4A2 to find your reference method and table 4D2A to find current carrying capacity, (unless it is Low smoke cable then 4E2A)

 