I thought I was VERY clear on that earlier. Maybe you should re-read post #195, #187, probably more.How so? Or is a logical choice. Its a decision point. One is a fact. Its a number. You wouldn't say, That's 1 Mile and then accept its 2, 3,5 or another number.
1 mile is an absolute measurement though, like 1 volt or 1 amp which clearly aren't 2 volts or 2 amps. I think the English language is sufficiently complex and flexible that when "one" is used in other contexts it does not necessarily exclude multiple options.
But even though I don't believe the additional earth rod in anyway deviates from BS7671, I do see the point you are making about covering oneself, even though I fail to see how anyone looking at such a case logically and with any knowledge of basic electrical principles could argue that it results in a situation different from bonding underground pipework, as already noted.
That's a bit evasive isn't it?
Perhaps, but then I can't say it's a scenario I've ever come across myself. It's one of those things which would not arise if we had some consistency in earthing methods.
So what is it if you loose your neutral? Is it TT then or just T?
I'd say it's faulty!
In your mind inferior? Its a perfectly acceptable system unlike what you are proposing.
Yes, in my opinion it is most definitely inferior to rely solely on the earth for fault-current path when you have a solid metallic path available with TN systems. And I will state that that
is my opinion, and not insist that it's a law, a regulation, or a statement of fact, although I do reiterate the fact that in other world electrical codes it is not permitted at all, so I'd say that my view of it certainly has some backing.
Tell you what, how about we don't call it an earth rod, and just bond a 5 ft. length of water pipe which happens to be driven into the ground but not used for supplying water anymore?
That's still an earth electrode as defined in 542.2.1(i) but you need to note 542.2.4 too.
So again, we're back to a non-electrical argument which is pointless. A purpose-made rod, or a bonded pipe running underground. Both provide an effective earth connection however you play off different BS7671 rules against each other.
BS7671 does not preclude it. If it did, then we would not be allowed to TT our outbuildings when the supply is TN-C-S.There is also the fact that having a rod at the installation is not changing the earthing system, so you would still be using one system.
I really hope you do not TT outbuildings that way. They should have separate Earths with any Earth in the cable (for example the armour on SWA) ony earthed at the end with the protective device (Reg 542.1.8).
Isn't that what Spin is referring to? The case where the supply & house are TN-C-S but the outbuilding is TT?
TT systems should also be done like this if a rod (or whatever earth electrode used) is placed at another location.
Hang on, if I'm reading that right you're now saying that a wholly TT system can't have more than one earth electrode either?
Surely you've come across cases of two or more rods interconnected to provide an improved earth?