542.1.1 states that a system should be one of the following TN-C-S, TN-S TT or IT. It states for TN-C-S systems (which I believe we are discussing here) that the MET will be connected, by the distributor, to the Neutral.
But nowhere does it say that there cannot also be a local earth electrode.
If you stick an earth rod in (remember pipe is not bonded to be a source of Earth and what if it had plastic incoming pipes anyway?) then you would have created a quasi system you would probably describe as T(NT)-C-S and thats not listed as a suitable Earthing system.
Adding an electrode to a TN-C-S system is no more making it some sort of TN/TT hybrid than is bonding to pipework or structural metalwork which is also an effective earth electrode.
The bonding to buried metallic pipework may not be done with the specific
intent of using that pipework as an earth electrode, but nevertheless it
is one. Electrically speaking, how is running a cable from the MET to an purpose-made earth rod any different from running a cable from the same MET to a length of buried metallic water pipe?
Remember everything the client side of the Meter (including the MET) is subject to 7671. This is why any Earth Rod would have to be connected to the PEM at or before the cutout.
Again, where does BS7671 say that an earth electrode may not be connected to the installation's earthing system, even though it is TN-C-S or TN-S?
But leaving aside the quasi-TN/TT argument, you could have the MET mounted right next to the service head and linked together by 6 inches of cable. Ignoring any arguments over the wording of BS7671 and just looking at it electrically speaking, how is there any significant difference between running a cable from the incoming PEN in the service head to a rod and running a cable to the same rod from the MET?
If I'm reading it right, Steptoe seems to be arguing that the former is acceptable (desirable, in fact), but the latter is somehow dangerous, which makes no sense.