Although the conductivity of the Massive Earth can vary region to region, area to area. Generally there is very little difference in the area surrounding a house, or even close outbuildings.Then there is the consideration that the impedance on a TN-C-S earth is nearly always going to be less than that of the Massive Earth.
Where it becomes a problem, is when there is a Supply neutral fault, which causes the installation earthing to become live.
If there is no reliable connection to the Massive Earth, such as when there are plastic services there will be no return path for the neutral.
A person could then introduce this return path by touching a live extraneous-conductive-part whilst in contact with the Massive Earth.
If your installation has a reliable connection to the Massive Earth, either through earthy services or a rod, this would become the return path for the neutral.
Unless there was a great difference in the conductivity of the Massive Earth in the area surrounding the house. A person touching a live extraneous-conductive-part whilst in contact with the Massive Earth, would not be in any real danger, because the neutral would be using a lower impedance path to return.
I would point out that the failure of a supply neutral is considered to be very rare, and is covered by ESQCR rather than BS7671.
At present when working to BS7671 we are not supposed to take such a fault into consideration.
Perhaps with more and more services being supplied in plastic, in future there will be a change to BS7671, and a requirement for a rod at TN-C-S installations.