With TNCS, if you loose a neutral then everything will stop working implying you have no power but you will have 230V potential at the Line connector and also at the neutral connector.Because your neutral and earth are linked all your CPC's will be at a higher potential. Since you have just exported the earth from your MET your class I accessories and bonded metalwork outside will now also be at a 230V potential waiting for someone to touch it.
'What about the RCD' I hear you cry. Well that will not trip as there will be no imbalance since the Earth and neutral are linked before the RCD so there is no imbalance. MCB will trip but a long time after you are already crispy.
'What about the RCD' I hear you cry. Well that will not trip as there will be no imbalance since the Earth and neutral are linked before the RCD so there is no imbalance. MCB will trip but a long time after you are already crispy.