The meaurement at the end of the cable coming from the origin DB will be the Zs for the Cct (Radial) coming from that board and should be with the earth connected, the sub main being a cct in its own right. Zdb for the next board must be taken with the incoming earth disconnected (GN3) as per Ze, this eliminates parrallel paths, although in practice you may well find that the Zs of the sub-main and the Zdb will be identical or very close.You'll need to show me where you got that one from.
as a note, it is now generally discouraged to take live Zs readings, preferable to calc using Ze + (r1+r2). i understand this is for two reasons 1. Less live working - ie is it neccessary under EAWR 89 as you can calc this easily from dead test measurements 2. Calcs give you safety margins and are as per design spec
This is an NICEIC 'general discouragement' and is pathetic.