I have just fallen off my chair laughing. You are having a laugh are you not? You are not being serious? Sorry if you are serious, I just wanted to check, before I move this to the student and learning section.
Anyway I have nothing better to do for a while so I will try to clarify.
Yes So the cpcs in the shed connect to what?
A MET Yes
What connects the MET to the means of earthing?
A earthing conductor. Yes
How many earthing conductors can an electrical installation have?
1 As many as required, depending on the installation
So as far as BS7671 is concerned, the shed is an electrical installation in its own right.
In the same way you could divide and call all parts separate
How many people veiw it that way?
Very few
Are you wrong for viewing it that way as ADS has
NO
If you think yes Back it up Please!!!
If you are insisting that it is a separate installation, then lets look at the REGS.
541.2
The earthing system of the installation may be subdivided, in which case each part thus divided shall comply with the requirements of this chapter.
542.1.8
Where a number of installations have separate earthing arrangements, any protective conductors common to any of these installations shall either be capable of carrying the maximum fault current likely to flow through them or be earthed within one installation only and insulated from the earthing arrangements of any other installation. In the latter circumstances, if the protective conductor forms part of the cable, the protective conductor shall be earthed only in the installation containing the associated protective device.
Now you could argue that you have stated that this forms the basis of your statements, however you have also argued that the Ze for this new consumer unit, is taken from that CU, it is not, Ze is, and always will be external to the supply.
Let me explain a little why this should never be confused.
If you design any installation some factors you will always need is type of earthing, type and size of supply and the expected or design loading of the supply.
Ze is a fixed measurement that is provided by the DNO, this figure given for TNC-S/PME is 0.35, and for TNS 0.8. You can not guess that these figures will be lower, but you can reasonably assume that it can not be higher. These figures are the figures used to design all large installs.
Now we have another problem, with any TNC-S the neutral conductor is still connected to earth, so why have we just banged a rod in?
Well, its all about potentials, and the differences this could cause, another reason why multiple rods are placed so that the potential from one does not effect the potential of another.
So what is this reading at the new CU? if its not Ze? Well if the CU is not at the origin of supply we must call it something else, simply because we have to treat this extension of the installation as part of the same system. It is earthed at multiple points, next time you extend a TNC-S, have a look at the readings you get to neutral.
Unfortunately the model forms, do not include all the information you would need to successfully complete a full EIC. Which is why some scheme providers have their own EIC forms, so that the details I have mentioned above can be correctly filled in.