All the outbuildings I do have a seperate earth TT so will be very different to ZE at house unless that is TT also.
I'm afraid I'm with Batty on this one.All the outbuildings I do have a seperate earth TT so will be very different to ZE at house unless that is TT also.
Im on the side of only ONE Ze,ADS,You cannot do this and comply with the definitions in BS7671.
There is no interpretation possible here with regard to this sorry.
We are talking here about definitions of values from the standard.
These are black and white.
You cannot deviate from the definitions, else you are talking about a different value.
Check the definition of an installation or a system.
Have you possibly not even considered mixed earthing systems in the outbuilding,g have you, any of you, perhaps?
You can only have one MET in an install.
Any other "main" earthing terminal is a BEMT, a Building Earth Marshalling Terminal.
Now unless this stays civil and polite, I will not post any more in this thread, and I will have no hesitation in reporting any abusive posts to the mods and the admins.
IF, we can all stay polite and civil, we can discuss this further.
HOWEVER, if you choose to do this, please back up your definitions with the appropriate regulations, definitions, or irrevocably sound science!
But Steps, if you stay true to form and don't 'export' the PME supplied earth to the outbuilding, how can you possibly have only one Ze - what about your 'rod'??Im on the side of only ONE Ze,after all, you only have ONE earthing conductor,
even if you have a TNCS with localised rodding its still only one MET at the source, doesnt matter where you earth your rods too, they are merely BEMT's.
has an Ra, NOT a Ze,No mixed earthing systems sidewinder - that's why you have to do what I describe.If you choose to 'rod' the outbuilding that is supplied by a distribution circuit off a TN system, then you have to keep the earthing systems seperate.
To do that, you would terminate the TN earth at a suitable point where it enters the outbuilding and keep it seperste from the TT earth that you are introducing to the outbuilding.
The outbuilding then becomes a seperate install with it's own earthing system - TT
How else could you possibly do it??
---------- Post Auto-Merged at 20:17 ---------- Previous post was made at 20:15 ----------
But Steps, if you stay true to form and don't 'export' the PME supplied earth to the outbuilding, how can you possibly have only one Ze - what about your 'rod'??
MY BLUEADS,OK no mixed earthing.
However, IF you have a water pipe from the house which is PME then you HAVE mixed earthing, end of, unless it is isolated by a section of polymer pipework.
Once it enters the 'outbuilding' it is bonded to the outbuilding MET - doesn't matter what happens to it before that, you are maintaining the 'outbuilding' equipotential zone.
Yes you do need to separate the earthing systems if you rod an outbuilding and that includes all of the possible earthy services and any structural steelwork, which would be impossible in many situations.
Don't get what you are trying to say - bit like saying you can't maintain a 'equipotential zone' at your house because next door has a different earthing system.
Yes that could be one way of separating the earthing systems if that were possible.
Not getting how it's not possible - it's the only way to do it.
The outbuilding does not become a separate system, check the definitions.
As you can only have ONE earthing system in an installation, I think, by it's own definition, if you TT an outbuilding, it becomes a seperate installation
What about Zs of the shed circuits??has an Ra, NOT a Ze,I can honestly see where you are coming from,
but, IMHO, if you are taking the earth from the house to the shed then you simply have a Zs at the shed end, whether or not you wish to even use it is up to you,
Ze would be at service head. your outbuilding would have a Ra. means of earthing for shed DB would be the rod. simple. (at least thats how i usually do it)MY BLUEIf you seperately 'rod' an outbuilding, how can you possibly treat the whole thing as one installation.
So, you record your Ze as 0.28 - because that's the measurement at the incommer and then what....
.....you measure the Zs of your socket outlet circuit in the outbuilding as 115 ohms (because of the rod) and record this on the same sheet??
What do you put on the form when it asks for Earthing Arrangements - do you tick two boxes?
Means of Earthing - tick both boxes again??
What's your PFC - 821 Amps.......not at the outbuilding it's not.
How can you possibly treat it as one system/installation?
Come on, where are all the 'I always Rod a shed' brigade............How do you do your forms????
---------- Post Auto-Merged at 20:52 ---------- Previous post was made at 20:50 ----------
What about Zs of the shed circuits??
my certs have a little box at the top for a DB/CU NOT connected directly at the source of the installation, with readings for Zs etc at that point.MY BLUEIf you seperately 'rod' an outbuilding, how can you possibly treat the whole thing as one installation.
So, you record your Ze as 0.28 - because that's the measurement at the incommer and then what....
.....you measure the Zs of your socket outlet circuit in the outbuilding as 115 ohms (because of the rod) and record this on the same sheet??
What do you put on the form when it asks for Earthing Arrangements - do you tick two boxes?
Means of Earthing - tick both boxes again??
What's your PFC - 821 Amps.......not at the outbuilding it's not.
How can you possibly treat it as one system/installation?
Come on, where are all the 'I always Rod a shed' brigade............How do you do your forms????
---------- Post Auto-Merged at 20:52 ---------- Previous post was made at 20:50 ----------
What about Zs of the shed circuits??
What about it mate?What about Zs of the shed circuits??
nothing, lots of installations have more than one source of supply,KME what would be the means of earthing for the shed?How do we connect to the means of earthing?
And whats wrong with having more than on origin?