OK - this comes from the man who wrote the NICEIC PV training course (nice guy, too).
The fact that the inverter will continue feeding for five seconds isn`t an issue to your other final circuits; providing the upstream RCD is double pole.
The reason is that, when the RCD operates, it breaks the neutral path out to the star point of the transformer, and therefore breaks the earth path.
The inverter is producing its voltage between phase and neutral; neither of which will now be referenced to earth.
So there is no fault path between live and earth - so there is no risk of that shock voltage continuing whilst the PV "over-runs"
I think I`m happy with that. It may not be ideal, but apparently it IS compliant.
p.s. Albert: sorry
The fact that the inverter will continue feeding for five seconds isn`t an issue to your other final circuits; providing the upstream RCD is double pole.
The reason is that, when the RCD operates, it breaks the neutral path out to the star point of the transformer, and therefore breaks the earth path.
The inverter is producing its voltage between phase and neutral; neither of which will now be referenced to earth.
So there is no fault path between live and earth - so there is no risk of that shock voltage continuing whilst the PV "over-runs"
I think I`m happy with that. It may not be ideal, but apparently it IS compliant.
p.s. Albert: sorry