Just finished a job, wiring up a football club and changing room...
And there is a bit of an argument between my boss and a sparky who is on the football committee... who is really P**Sing every one off!
My boss recons that we only need to bond to the main bonding to services (OIL & Water) and only cross bonding on the boiler.
The other spark (who is nothing to do with the installation) is saying that we should be cross bonding all sinks in the changing rooms, and kitchen as well??
I am only the apprentice, who is learning, so would like to know that the "Done" thing is.
Many thanks
seajayess
Senior Member
Joined
May 28, 2008
Messages
272
Reaction score
0
wired to 17th. edition only main equipotetial bonding required as long as disconnection times can be met, water / gas / oil / steel structure CJS
danny7299
Well-known member
Joined
Apr 6, 2008
Messages
880
Reaction score
0
Location
Leicestershire
i though that maybe the case as most things are now RCD protected,
Regarding structre bonding do you just bolt it to the metel work? or do you need multipull points?
Admin1
Forum Founder
Joined
Feb 6, 2008
Messages
10,278
Reaction score
-1
We talking a Proper catrering kitchen here? (as it is a rugby club).
I know in domestic there are no requirements to Supp bond a kitchen.
But in commercial, especially where there are a lot of fixed or hard standing metalwork work areas, where a person can touch an appliance and the metal work at the same time etc, I, personally WOULD Supp bond them.
But, Let's see what the other's say.
Admin1
Forum Founder
Joined
Feb 6, 2008
Messages
10,278
Reaction score
-1
Ah, If it RCD or RCBO protected and Disc times are met - then we are talking about a different kettle of fish.
seajayess
Senior Member
Joined
May 28, 2008
Messages
272
Reaction score
0
Because RCD RCBO provide additional protection that would be required if disconnection times cannot be met and you have already provided it CJS
Admin1
Forum Founder
Joined
Feb 6, 2008
Messages
10,278
Reaction score
-1
Yes, But - As said, ONLY if your diconnection times are met. :)
Joined
May 7, 2008
Messages
11,429
Reaction score
426
Location
Sunny Plymouth
Consider metal work tops/ sinks etc etc and faulty appliance making live connection to surface but not necessarily to neutral or earth of appliance.... I would bond back to easily accessible socket as a minimum. As I understand it RCBOs are additional protection in these circumstances and should not be considered main protection, but would have to look up extranuous conductive parts to give a more definitve answer. Its a bit like bonding to frontplate of metal sockets, light switches etc. I also used to work with someone who was nearly killed by such circumstances whilst visiting a chinese factory - the chinese guy he was with died.