OK,
Finished a PIR today, reports etc. still to do, may post some pics if I get a chance a bit busy at the moment with several things, some good some very bad!
OK. Industrial/commercial premises. PME supply.
Incoming mains, fuses must be equal to or less than 100A, industrial thus I would guess BS88's. Taking these as 100A.
Reason for rating, direct current metering, anything >100A requires CT's.
Straight into an old panel board. No on site HV transformer.
Main fuse switch (MS) rated at 600A, 5 sub main switch fuses/fuse switches (FS) etc. in panel board, with a few other bits not relevant.
FS: 2 rated @ 200A (FS4 & 5) , 3 rated @ 100A (FS1-3).
All 3ph.
Fuses as follows:
DNO: 100A
MS: 600A
FS1: 63A sub main feeding 6 way TP board with Final Cct's & 3 further sub mains, including 3 to buildings remote to the origin
FS2: 30A sub main feeding site boiler/heating controls no final cct's all heating/boiler controls cct's
FS3: Spare
FS4: 200A sub main feeding separate building
FS5: 150A sub main feeding in building DB final cct's only
I'm not asking for advice, I know my results & my responses, (our! ) just posting this for comments and to add to the "knowledge base" working on the PIR paperwork & report now.
Just looking for the "learners" to comment for their benefit. I'm NOT going to post my comments etc. until this has been debated a bit for the "trainees" / "inexperienced" to discuss this with those "in the know".
Trying to help?
Paul
p.s. may not be able to check back too often, but lets go with the flow.
There is another who knows the install here...
Finished a PIR today, reports etc. still to do, may post some pics if I get a chance a bit busy at the moment with several things, some good some very bad!
OK. Industrial/commercial premises. PME supply.
Incoming mains, fuses must be equal to or less than 100A, industrial thus I would guess BS88's. Taking these as 100A.
Reason for rating, direct current metering, anything >100A requires CT's.
Straight into an old panel board. No on site HV transformer.
Main fuse switch (MS) rated at 600A, 5 sub main switch fuses/fuse switches (FS) etc. in panel board, with a few other bits not relevant.
FS: 2 rated @ 200A (FS4 & 5) , 3 rated @ 100A (FS1-3).
All 3ph.
Fuses as follows:
DNO: 100A
MS: 600A
FS1: 63A sub main feeding 6 way TP board with Final Cct's & 3 further sub mains, including 3 to buildings remote to the origin
FS2: 30A sub main feeding site boiler/heating controls no final cct's all heating/boiler controls cct's
FS3: Spare
FS4: 200A sub main feeding separate building
FS5: 150A sub main feeding in building DB final cct's only
I'm not asking for advice, I know my results & my responses, (our! ) just posting this for comments and to add to the "knowledge base" working on the PIR paperwork & report now.
Just looking for the "learners" to comment for their benefit. I'm NOT going to post my comments etc. until this has been debated a bit for the "trainees" / "inexperienced" to discuss this with those "in the know".
Trying to help?
Paul
p.s. may not be able to check back too often, but lets go with the flow.
There is another who knows the install here...