Hi,First off, I am not sure i understand the description really, for example you say that "fs 1" is a 63A submain. What do you mean by a 63A one? I thought you might mean it had a 63A isolator/switchfuse supplying it, but you have already said that Fs 1 has got a 100A fuse, so is it a 63A switchfuse that someone has put a 100A fuse in? I am baffled now??
OK, BTW the PIR was 71 pages!
I can't find this in the final PIR so we may have coded it 1 & rectified, but IIRC your description above is correct.
I will try to find my site notes as soon as I can.
Anyway, from what i can understand of your description i shall have a go??!!!!!!!
1, The DNO cutout has, [as you have deduced from the fact that the installation has "whole current metering"] 100A fuses in it, BUT HAS IT??
The DNO cut out did have 100A fuses, the metering is whole current rather than CT, thus whole current is cappeed at 100A/ph.
Why then, is the rest of the install so massive, especially as it feeds more than several tenants, and all on 100A board fuses!!. You say they have never blown in 12 years?? How have they never blown?? How do you know there are not bits of brass bar in there instead of fuses!!, are the seals still there??
The install had a change of use 12/13 years ago.
The DNO fuses are 100A BS88's.
Is there any indication as to what the maximum or usual demand of the entire installation is and would this in you opinion be suitable, or even possible for a mere 100A supply??
We did not undertake a maximum demand calculation formally. The installation use has decreased over the last fewe years after reaching apeak between the change of use and then.
It was reported that the fuses had not blown.
What size are the tails from the cutout to the internals of the panel? are there any signs of overheating??
The tails were 35mm sq. No evidence of overheating
2, Are you saying that FS1 [the 63A jobbie] has a 100A fuse in it?? As the supply is TN/C/S and it feeds buildings remote to the origin, what earthing/bonding arrangements are in place for the remote buildings, and are they suitable??
This building was not part of our PIR, however it is fed from the origin of the supply, we did not have full access or remit to PIR this building unless we did this as a freebie!
This building may have other links between itself and the building housing the origin as it was originally part of the same undertaking. It is now sub let.
It may well, in fact, probabaly have a 100A fuse in it if that is what my OP says, this is nearly a year ago and my memory is NOT that good, though this may be in my day book.
The remote building was excluded from the PIR thus coded a 2 as was the bonding etc.
The remote building has considerable structutal steel so it may have a very low local earth path.
However I cannot fully comment as it was excluded and under a maintenance contract with a large regional electrical contractor who obviously (well the guys they sent there) were not worried or "up" on the full requirements and status of the supply.
They may have missed the fact that it was a sub main as it had local landlord metering and if I had reasonable pics you may have missed this too.
Remember the DNO cut out can be remote to the metering and the main db for the install.
3,If FS2 is a 30A sub main, then are you saying [i think] it has a 100A fuse in it?
Probably yes, again I'd have to check my site notes as it may have been re-fused or decommissioned.
4, FS4 [remote building] Same comments as regarding earthing/bonding arrangements.
In which case see above, sorry.
5, if FS5 is a "150A submain", why has it got from what i can make out, a 200A fuse??
Same again really as above.
As the fuses are all so huge, is the cabling equally proportioned, and suitable to be protected by these sizes of fuse?
Yes IIRC the sub mains were cable sized in accordance with the capacity of the origin isolators.
However the fuses installed by persons unknown did not relate to the FS sizes or the cable sizes or the requirements etc.
What about ELI and disconnection times?? As Zs x Ia must be less than Uo, and this seems to be a fairly huge installation, how have they managed to achieve the required disconnection times?? especially if they have TT'ed the remote buildings.
I doubt the remote buildings are TT'd they are probably all within the EEZ for the main install in effect, bar one or two points which may come up later.
As the fuses are so huge they are going to need very very low ELI values, unless of course they have suitable small rating devices protecting the final circuits. Then again i suppose, if all the sub main cables are of suitable size to match the fuses protecting them [huge] and have therefore very low impedance, and they have got sensibly sized fuses or whatever protecting the final circuits they might just be ok, at least as regards the final circuits anyway. Still leaves the bonding and earthing arangements and if bits are TT'ed the requirement for all poles to be isolatable.
The ELI values were quite low IIRC, the PSCC & PEFC are capped at 25kA by the DNO anyway in this area.
Did not the person that installed this lot make his own enquiries as to the suitability of the incoming supply??, and if he did, why the massively overrated accessories.
He almost certainly did as the install was designed by probably a Chartered Electrical Engineer who could probably knock my knowledge into a cocked hat!
Thing is since the original install was designed and constructed, there has been a change of use.
Also that change of use allowed a supply downgrade, thus this will have been undertaken by the DNO.
IT is very doubtful that they will have questioned the original install at that stage as the building was taken over quickly after the original occupier moved out, due to the design and management of the original install.
The bodged jobs have been done in the intervening 12 (ish) years.
Personally, i would be trying to work backwards to ascertain the the max demand required for what ever it feeds, and compare this with the supply capacity, and then go from there, with properly rated protective devices. I cannot for the life of me see that this supply is suitable and there will be NO CHANCE that the remote buildings anr bonded correctly for the type of supply, and disconnection times will be a joke i would think.
I doubt there is an issue with the max demand else the mains fuses would have blown, which it was reported that they had not.
We proposed to work backwards, however the client did not want any remedials doing.
This will rear its head within the next few months as the insurance is due again!
Unless the client has paid someone to sign off our code 2's then he will not get business insurance with the same insurer, and has been winging it for best part of a year now!
Be kind to me!!!! I am only a beginner!!!!!!!!!!!!!!!!!!!!
I don't do kind I do IMHO fair!
john