you pressing the test buttons simultaneously is not going to happen and with such a short time span its critical do you not thinkThanks Albert:The ramp test, however, wouldn`t provide a time to trip; just the current necessary.
I was thinking of using both our MFTs, on the 10mA range, at the same time. That would put 20mA on it, and one of the testers would pick up the trip time; the other would be a lot higher, if "test" was pressed first. However, SW has another way of doing this; using the 1653.
Supply PFC WAS >10KA; as we had more than that at the sub-board, IIRC
Don't need to press simultaneously.you pressing the test buttons simultaneously is not going to happen and with such a short time span its critical do you not think
Point 1 not blown DNO fuses, in 12 years the install is about 34 years old changed use 12 years ago (ish) I believe the incomer was changed about this time, downsized to save the new occupier cost, but the install was not assessed & addressed to accomodate.SW some of my stabsthe dno A ratings and the MS A Rating is surely not an issue?
this arrangement happens 99% of the time surely?
while you say its not blown the dno's in 12 yrs the design is flawed should the buildings change electrical requirements simply the capacity is not there to supply the demand
FS1 is likely not to discriminate as other sub boards likely supplied by 63a ?
FS2 can't see an issue
FS3 none
FS4 all done to insufficent supply via dno's fuses
FS5 as above
as i know you like your fault current discussions i'm guessing this is more of your concerns and is where i'm in for the lesson.
i should know all this having done mostly industrial with design too :coat
Yes, but, KME remember WPD limit the max PFC on such supplies to 25kA by design.Thanks Albert:The ramp test, however, wouldn`t provide a time to trip; just the current necessary.
I was thinking of using both our MFTs, on the 10mA range, at the same time. That would put 20mA on it, and one of the testers would pick up the trip time; the other would be a lot higher, if "test" was pressed first. However, SW has another way of doing this; using the 1653.
Supply PFC WAS >10KA; as we had more than that at the sub-board, IIRC
Hi yourself. Flippin` heck; this was a while ago - but I`ll see how much I recall as we go along (Sidewinder has the paperwork for this, not I )Hi,First off, I am not sure i understand the description really, for example you say that "fs 1" is a 63A submain. What do you mean by a 63A one? I thought you might mean it had a 63A isolator/switchfuse supplying it, but you have already said that Fs 1 has got a 100A fuse, so is it a 63A switchfuse that someone has put a 100A fuse in? I am baffled now??
The installations "change of use" means that, as far as we could ascertain, 100A/phase was in excess of their requirements, at the time of inspectionAnyway, from what i can understand of your description i shall have a go??!!!!!!!
1, The DNO cutout has, [as you have deduced from the fact that the installation has "whole current metering"] 100A fuses in it, BUT HAS IT??
Why then, is the rest of the install so massive, especially as it feeds more than several tenants, and all on 100A board fuses!!. You say they have never blown in 12 years?? How have they never blown?? How do you know there are not bits of brass bar in there instead of fuses!!, are the seals still there??
It appeared that, as I referenced above, following the change of circumstances, a mere 100A was more than adequate.Is there any indication as to what the maximum or usual demand of the entire installation is and would this in you opinion be suitable, or even possible for a mere 100A supply??
iirc, the metering and HED are within the panelboard; supply was via busbar, I think? No overheating signs apparentWhat size are the tails from the cutout to the internals of the panel? are there any signs of overheating??
I can`t honestly remember. Sorry. Maybe snakehips can.....2, Are you saying that FS1 [the 63A jobbie] has a 100A fuse in it?? As the supply is TN/C/S and it feeds buildings remote to the origin, what earthing/bonding arrangements are in place for the remote buildings, and are they suitable??
Wow! good post John; even if it IS an old thread, and I can only just recall the layout of the intake room.3,If FS2 is a 30A sub main, then are you saying [i think] it has a 100A fuse in it?
4, FS4 [remote building] Same comments as regarding earthing/bonding arrangements.
5, if FS5 is a "150A submain", why has it got from what i can make out, a 200A fuse??
As the fuses are all so huge, is the cabling equally proportioned, and suitable to be protected by these sizes of fuse?
What about ELI and disconnection times?? As Zs x Ia must be less than Uo, and this seems to be a fairly huge installation, how have they managed to achieve the required disconnection times?? especially if they have TT'ed the remote buildings.
As the fuses are so huge they are going to need very very low ELI values, unless of course they have suitable small rating devices protecting the final circuits. Then again i suppose, if all the sub main cables are of suitable size to match the fuses protecting them [huge] and have therefore very low impedance, and they have got sensibly sized fuses or whatever protecting the final circuits they might just be ok, at least as regards the final circuits anyway. Still leaves the bonding and earthing arangements and if bits are TT'ed the requirement for all poles to be isolatable.
Did not the person that installed this lot make his own enquiries as to the suitability of the incoming supply??, and if he did, why the massively overrated accessories.
Personally, i would be trying to work backwards to ascertain the the max demand required for what ever it feeds, and compare this with the supply capacity, and then go from there, with properly rated protective devices. I cannot for the life of me see that this supply is suitable and there will be NO CHANCE that the remote buildings anr bonded correctly for the type of supply, and disconnection times will be a joke i would think.
Be kind to me!!!! I am only a beginner!!!!!!!!!!!!!!!!!!!!