I was prompted to post this after reading the post started by electrcian786 British Gas/ DNO problem.
TN earth systems give earth fault loops below 1 ohm (Ze). TT earth systems fault loop is over 1 ohm (Ra). I am deliberately avoiding quoting the typical values because it is not critical to my post.
Fault disconnection times in the regs are reliant on keeping within max Zs values. TN systems Ze are generally low enough to allow earth fault loops to be within the tabulated values for the final circuits. TT systems will generally push Zs over tabulated max Zs values.
Now to the point of my post.
I am specifically referring to EARTH fault loops here as faults within the lines are not affected by earth impedance (overload or short circuit). In order to achieve disconnection of a fault to earth on a TT system an RCD is needed. Without an RCD the earth fault loop impedance will be too high to rely on the fuse to disconnect the fault in time. This raises several questions that confuse me.
DNOs appear to be getting complacent about providing an earth and are inconsistent in how they respond to requests for earth systems to be installed or even verified.
DNOs appear to be reluctant to install earth systems and are more than accepting for a customer to install their own earth rod.
On the face of it, TN systems under previous editions of the regs, where split load fuseboards were the default choice, relied on good TN systems to be in place, else the safety of non-RCD protected circuits would be compromised under earth fault conditions.
So, given the advent of 17th edition and the total RCD protection (30mA) of all circuits, do we really need TN earths any longer? Should we be TT by default? Am I missing something?
Just to be clear for all those students reading this thread and be certain that this is not a talkdomestic electrics only thread:
In DOMESTIC installations is a TT earth any safer or less so than aTN?
In DOMESTIC situations, EXCEPT WHERE A REG OR MANUFACURER of an item or accessory specifically prohibits, we can adopt 30mA protection on every circuit...
TN earth systems give earth fault loops below 1 ohm (Ze). TT earth systems fault loop is over 1 ohm (Ra). I am deliberately avoiding quoting the typical values because it is not critical to my post.
Fault disconnection times in the regs are reliant on keeping within max Zs values. TN systems Ze are generally low enough to allow earth fault loops to be within the tabulated values for the final circuits. TT systems will generally push Zs over tabulated max Zs values.
Now to the point of my post.
I am specifically referring to EARTH fault loops here as faults within the lines are not affected by earth impedance (overload or short circuit). In order to achieve disconnection of a fault to earth on a TT system an RCD is needed. Without an RCD the earth fault loop impedance will be too high to rely on the fuse to disconnect the fault in time. This raises several questions that confuse me.
DNOs appear to be getting complacent about providing an earth and are inconsistent in how they respond to requests for earth systems to be installed or even verified.
DNOs appear to be reluctant to install earth systems and are more than accepting for a customer to install their own earth rod.
On the face of it, TN systems under previous editions of the regs, where split load fuseboards were the default choice, relied on good TN systems to be in place, else the safety of non-RCD protected circuits would be compromised under earth fault conditions.
So, given the advent of 17th edition and the total RCD protection (30mA) of all circuits, do we really need TN earths any longer? Should we be TT by default? Am I missing something?
Just to be clear for all those students reading this thread and be certain that this is not a talkdomestic electrics only thread:
In DOMESTIC installations is a TT earth any safer or less so than aTN?
In DOMESTIC situations, EXCEPT WHERE A REG OR MANUFACURER of an item or accessory specifically prohibits, we can adopt 30mA protection on every circuit...