Im doing some work in a house that is 40 miles away so i am trying to keep the travelling down.
no earth at the existing board (middle of the house) so i found a route out to the rear garden.I told the customer(a mate) that he needed to put a rod in no problems
it went down about 18 inches then hit rock,,,,pulled it out drilled down through rock another 12inches......
i took a reading and got 858 ohms
i am back there tomorrow to change the board (dual) but may not have time to relocate the rod
would you guys be happy to use the rod in the mean time until i am back there in a few weeks on another local job ????
858 x 0.03 = 25 so well within the rquirements of reg 411.5.3
its just the stability issue.
when i did a zs on the existing board i got 575 ohms on trip lock !!!!! better than the rod..