In the case of MCBS, they have everything to do with it, as I said, they are all or nothing.yes i know what the "O" stands for, but L/N Loop eh! Earth faults need a very low ohm range to make sure you get high enough currents to trigger off the MCB before 0.4 seconds. ie before someone dies (in theory)
Overcurrent is different. A flow of 30A may flow through a 10A MCB but will not trigger off the MCB before 0.4 seconds cos the fault is not seen as passing through a person for eg.
What i think you are getting at is short circuit protection ie a direct short from live to neutral and not to earth.
Well no.....All the Zs figures are to do with the 0.4 second Diss time for earth faults and have nothing to do with short circuit faults. But if you can prove they do, then do it.