:slap
:slap
And that's where the Zs value comes into play.I think the confusion is that the OP did not state if the installation was TT or TN, with 411.5 dealing with TT and table 41.5, and 411.4 dealing with TN and table 41.3 to be read with 411.4.9 where it states "Where an RCD is used to satisfy the requirements of Regulation 411.3.2.2 the maximum values of earth fault loop impedance in Table 41.5 may be applied for non-delayed RCD's to BS EN 61008-1 and BS EN 61009-1 for a nominal voltage of 230V. In such cases, an overcurrent protective device shall provide protection against overload current and fault current in accordance with chapter 43"
No Tim, i don't lol.I think you need to check up on the definition of Zs
So lets get back to the first post by LNRDF01, is it ok or not !!!!!I did a test and inspection on a domestic premises and noticed the RCBO's installed were type C, these have a much lower Zs value than the type B, apart from that i always assumed type C's were for circuits with equipement that had a high start up current. Are type C RCBO's acceptable in domestic installations?.
If you look at the curves Tim, move from the instantaneous to the left, If the Live loop is high teh the disconnection quickly becomes seconds, put that into the Adiabatic and see if the Thermal Constraints of the cable are satisfied.And I would agreeThe Onsite guide page 56 Table 7.1(i) lists a 32 Amp RCBO Type C Ring final circuit protective device.
For TN-C-S system it gives a max circuit length of 133 mtrs and then you note sc adjacent.
A look on page 65 at the notes shows sc to mean "Limited by LINE to NEUTRAL loop impedance (short circuit)
Im not referencing the L-N loop as Zs, im saying you can use the Zs values for a MCB in regard to Thermal Constraint's, i think its a lack of understanding by others, otherwise they would of understood what was being said.Yes thats true the L to N Loop not Zs
$park I think we are fully aware what you putting over with regard to using the Zs value for a MCB in regard to Thermal Constraint's, however the first post asked if a 32A C Type RCBO feeding a Ring Main wired in 2.5mmIm not referencing the L-N loop as Zs, im saying you can use the Zs values for a MCB in regard to Thermal Constraint's, i think its a lack of understanding by others, otherwise they would of understood what was being said.