Hi
Firstly, I am not a spark, merely mechanically qualified to trade, struggling with an electrical question at college.
Could anyone assist with this question ?.
A 230vac circuit with a Zs of 0.6 ohms on a TN system.
5kw load/25 amp type D MCB.
Would a 0.4ms be possible ?.
I have used
25x20 =500
230/500=0.46
0 46x0.8 = 0.368
To me the answer may be yes as 0.368 is less than 0.4 seconds, but I'm a bit lost.
I don't understand the tables showing 0.4/5s trip times for type D mcbs.
even more confusing is there are different figures used on the 2 tables below.
Can anyone help out ?.
Many thanks.